e57
- San Francisco, CA
Thats fine.... I'll allow fatique.I'm tired of wasting my time.
I have offered to agree to dis-agree a few times - we can leave it at that.It's not fatigue, just utter disgust at failing to see absolutely any reason in just about anything you're saying.
It is not that way here yet - I'm not on the '08 cycle yet.We're told to bond something, which in a grounded system will eventually imply that it will be connected to the service neutral. This is such a basic concept that it bears no discussion - yet somehow, you have a problem with it.
It is plain that all service enclosures, one way or another, better wind up connected to the system neutral. You insist that "it's not that way here."
Lets play nice... I have not made any personal attacks on you... Nor will I.You're either not communicating very well, spouting nonsense for confusion's sake, or dangerous; you're far enough from my house I can safely not care which it is. So be it.
If this quote (the Article 100 definition of ground fault current path) is intended to be language supporting your point of view that all paths must be low impedance, I don't follow you, because "An" is singular. So this definition says one path is adequate.An electrically conductive path from the point of a ground fault on a wiring systemthrough normally non-current-carrying conductors, equipment, or the earth to the electrical supply source.
Key words - bond together. (bond all the metal together)It's not a personal attack, it's a fact. If you have exposed non-current-carrying metal housing service conductors that is not electrically connected to the service neutral, you have a shock hazard. It is dangerous and has been a code violation for many cycles. I have pointed out the code sections to you and you choose to ignore it.
In the 2005,
250.92 tells us to bond all the metal together.
250.24 tells us to connect the metal to the system neutral.
(3) Bonding of Electrical Equipment.
Non-current carrying conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected together and to the electrical supply source in a manner that establishes an effective ground-fault current path.
This is further qualified here:Ground-Fault Current Path.
An electrically conductive path from the point of a ground fault on a wiring system through normally non-current-carrying conductors, equipment, or the earth to the electrical supply source.
Let me address another point here to someone else:(5) Effective Ground-Fault Current Path.
Electrical equipment and wiring and other electrically conductive material likely to become energized shall be installed in a manner that creates a permanent, LOW-impedance circuit facilitating the operation of the overcurrent device or ground detector for high-impedance grounded systems. It shall be capable of safely carrying the maximum groundfault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source. The earth shall not be considered as an effective ground-fault current path.
Please pay close attention to the words in bold:wwhitney said:If this quote (the Article 100 definition of ground fault current path) is intended to be language supporting your point of view that all paths must be low impedance, I don't follow you, because "An" is singular. So this definition says one path is adequate.
Does the neutral (AKA Grounded service conductor) fit the describtion in bold? Odds are it does not. Nor is it specifically listed by inclusion in the list under 250.92(B) 1~4, or through an FPN. That is my issue with the 'one end' that is not bonded. The other non-bonded end is bonded by the tuna sandwich.Ground-Fault Current Path.
No, it does not fit the description in bold. Instead, it fits the last part of the phrase, the "electrical supply source". The whole point of bonding is to provide a low impedance current path to the grounded service conductor, and hence back to the transformer.Please pay close attention to the words in bold:
I don't understand this statement. The grounded service conductor is explicitly mentioned in 250.92(B)(1) "Bonding equipment to the grounded service conductor in a manner provided in 250.8"Nor is it specifically listed by inclusion in the list under 250.92(B) 1~4, or through an FPN.
It would be a shame, if that end were in danger of ever becoming detached from the end with the bonding bushing on it. :roll:That is my issue with the 'one end' that is not bonded.
Yes - it does not fit the description in bold. (Not trying to get sarcastic with you - but it is what has been referred to as the "tuna sandwich" earlier.) The electrical supply source is in two places, IF the grounded service conductor is connected in each enclosure. (Meter pan, and the main disconnecting means.) Current will not choose to take one path to the source over the other - it will take both. Correct? (Think about that objectively. Along one weaker path, fault current may even damage or destroy the other.)No, it does not fit the description in bold. Instead, it fits the last part of the phrase, the "electrical supply source". The whole point of bonding is to provide a low impedance current path to the grounded service conductor, and hence back to the transformer.
Cheers, Wayne
It just might - in the OP - my initial response mentioned that them things are not always acepted everywhere. Being mealy tin it just might turn into a Dali painting...It would be a shame, if that end were in danger of ever becoming detached from the end with the bonding bushing on it. :roll:
You might get more of MY money from creating and listing a range of sizes of isolating fittings for use with RMC. Say 2" female to 2" male with insulation between them. Problem that I see would be over. You could even approach the NEC during ROP's and seek to mandate it's use.I think I'll get to work on a bonding device to attach to the center of the nipple; even with a bonding bushing in either end, it's no guarantee that the offset portion won't mutiny and detach itself from the ends...
Yes. So what?Current will not choose to take one path to the source over the other - it will take both. Correct?
Wrong, wrong, wrong. Both sides are bonded. One side is bonded more definitively as required by 250.92(B).One side of the nipples current paths fits the definition of "bonded" (an effective fault current path) - the other end merely fits the definition of "Grounded" as allowed by 250.142.
And in this case - the "bonded" end is not even the path toward the source. The fact is it will take both paths. Correct?
Then make a proposal. The NEC doesn't require it now.e57 said:IMO both sides should be a "bonded" effective fault current path.
Sure. So why is that a problem?Current will not choose to take one path to the source over the other - it will take both. Correct?
While a high impedance fault can over time cause damage from the heat dissipated, if it is parallel to a low impedance fault, the low impedance fault is going to get cleared first, one way or another (via the OCPD, or via burning up one of the service conductors).(Think about that objectively. Along one weaker path, fault current may even damage or destroy the other.)
In common usage, "bonded" is a term that applies to an object, not a path.One side of the nipples current paths fits the definition of "bonded" (an effective fault current path) - the other end merely fits the definition of "Grounded" as allowed by 250.142.
Quote:
Yes. So what? You have two paths - both should provide effective continuity for fault current IMO. Otherwise you have applied a label as "bonded" but not in practice.
Wrong, wrong, wrong. Both sides are bonded. One side is bonded more definitively as required by 250.92(B). This is that label - but not in practice item again - 'Bonded in name only'
Think about this objectively. OK...
Scenario #1: A ground fault occurs 200' downstream from the service. The fault current arrives at the service, and then splits between the neutral and the nipple. The current is halved on both paths. Explain the danger - and leave out the loose locknut bologna, I'm not interested. Tight locknuts installed per code. So per code I am allowed to also have concentric/eccentric/oversized knock outs and reducing washers - yep.... Looking at possibly ~10k AIC? Current takes both paths acing as a choke on the neutral - takes longer for the main OCP to trip.
Scenario #2: A fault occurs inside the nipple. It is connected to the neutral in the service disconnect. It is also bonded to a lesser degree to the meter socket can as well. Explain the danger. (As you well know I'm not going to call the "lesser degree" "bonded" - for the sake of discussion - lets call it "connected") So per code I am allowed to also have concentric/eccentric/oversized knock outs and reducing washers - yep.... Looking at possibly >10k AIC? Current takes both paths acing as a choke on the neutral - there is main OCP to trip. Damage occurs on the current path at the merely 'tightly connected' locknut - arcs - possibly causing damage to the ungrounded service conductors inside - this possible fault path will either blow open, causing further destruction to equipment, or it will hold until another connection opens. (Wow - sounds like fun.)
Also think about the fact that your blessed bonding bushing creates a third, not a second path. The locknut on the bonding bushing side is also a path. You know - you're right... But the locknuts are not required to be "bonded" - the raceway is. The locknuts are "grounded" to both the raceway, and the enclosure, both of those items are connected in a direct path by a conductor sized by 250.66, AND in a direct path to the item mentioned in 250.92(B)1 in that enclosure, reducing the danger explained in scenario #2 above.
Multiple paths of bonding are not a bad thing. More paths equal lower resistance. But not all paths are created equal - are they?
Then make a proposal. The NEC doesn't require it now. I just might... If we were having this discussion last year and it was on top of my priorities when I submitted 2 other proposals - I might have.
That is what I see as a problem. It is used as a label - one that has been disconnected from its meaning.In common usage, "bonded" is a term that applies to an object, not a path.
Cheers, Wayne
Bonding (Bonded). The permanent joining of metalliccurrent likely to be imposed.
parts to form an electrically conductive path that ensures
electrical continuity and the capacity to conduct safely any
That makes responding harder.My responses in red.
You have two paths - both should provide effective continuity for fault current IMO.Current will not choose to take one path to the source over the other - it will take both. Correct?
Yes. So what?
Opinion.This is that label - but not in practice item again - 'Bonded in name only'Wrong, wrong, wrong. Both sides are bonded. One side is bonded more definitively as required by 250.92(B).One side of the nipples current paths fits the definition of "bonded" (an effective fault current path) - the other end merely fits the definition of "Grounded" as allowed by 250.142.
There is no choke on the neutral. All circuit conductors are in the same conduit, and that conduit is bonded. A parallel bonding path will only serve to clear the fault a touch faster, not slower.So per code I am allowed to also have concentric/eccentric/oversized knock outs and reducing washers - yep.... Looking at possibly ~10k AIC? Current takes both paths acing as a choke on the neutral - takes longer for the main OCP to trip.Scenario #1: A ground fault occurs 200' downstream from the service. The fault current arrives at the service, and then splits between the neutral and the nipple. The current is halved on both paths. Explain the danger - and leave out the loose locknut bologna, I'm not interested. Tight locknuts installed per code.
You will have to find the service that this has occurred in to sway the CMP or myself. If the service conductors are faulting to the nipple, I do not expect the nipple to remain pristine, destruction will happen. With that bonding bushing connected to it, it will continue to dump it's fault current into the service neutral well past it's useful (reusable) life. That's about all we can ask of the nipple, no?This possible fault path will either blow open, causing further destruction to equipment, or it will hold until another connection opens.Scenario #2: A fault occurs inside the nipple. It is connected to the neutral in the service disconnect. It is also bonded to a lesser degree to the meter socket can as well. Explain the danger.
Quit acting stupid. You know damned well I was referring to the fact that the raceway is also bonded by the locknuts securing that raceway to the can.You know - you're right... But the locknuts are not required to be "bonded" - the raceway is.Also think about the fact that your blessed bonding bushing creates a third, not a second path. The locknut on the bonding bushing side is also a path.
This is where I point to when I say that you are attempting to confuse the issue. Use proper terms. I'll let you call it "connected" when you want to communicate that you don't trust the bonding connection, but flopping over to "grounding" is useless.The locknuts are "grounded" to both the raceway...
No, and no two paths between anything have ever been required to be equal. Your issue is not the presence of two paths, so why keep harping on it? You're just confusing your case.But not all paths are created equal - are they?Multiple paths of bonding are not a bad thing. More paths equal lower resistance.
Only you have disconnected it from it's meaning.That is what I see as a problem. It is used as a label - one that has been disconnected from its meaning.
You, of all people, advocating inhumane treatment?!?I think it's time to lock you 2 in a room together and turn up the heat.
Look George, It is obvious that we (you and I) are not going to agree. But please knock of the 'stupid' type comments - they only serve to belittle yourself. Really whats next 'momma jokes'?Quit acting stupid. You know damned well I was referring to the fact that the raceway is also bonded by the locknuts securing that raceway to the can. (1)
This is where I point to when I say that you are attempting to confuse the issue. Use proper terms. I'll let you call it "connected" when you want to communicate that you don't trust the bonding connection, but flopping over to "grounding" is useless. (2)
~Your issue is not the presence of two paths, so why keep harping on it? You're just confusing your case. (3)
Only you have disconnected it from it's meaning. (4)
Now ask yourself. Without the neutral, is the metallic conduit path "Bonded"?
Bonding (Bonded). The permanent joining of metallic parts to form an electrically conductive path that ensures electrical continuity and the capacity to conduct safely any current likely to be imposed.
OK, good, your issue is the two paths. You obviously feel that the difference in requirements for the two ends of this service nipple presents a hazard. However, the NEC and the community does not see it that way. Do you have any evidence or examples of this hazard? Why is having a higher impedance fault path in parallel with a low impedance fault path a hazard?[*]My issue IS the two paths, ALWAYS has been from the very beginning.
I think the discussion will be easier to follow if you adopt the common usage of "bonded" as refering to an object, not a path. I would suggest a different terminology for what you are advocating, like "I feel it is not enough for the nipple to be bonded, bonding should be required at both ends."One fits the definition of bonded, the other does not.
As a definition of "bonded", this NEC definition leaves a lot to be desired. It is really only a definition of "bonding". The definition of "bonded" based on this is "having bonding to the common reference point", which would be the GEC or thereabouts.Bonding (Bonded). The permanent joining of metallic parts to form an electrically conductive path that ensures electrical continuity and the capacity to conduct safely any current likely to be imposed
This doesn't really matter, because the grounded service conductor is explicitly allowed to be used for bonding in 250.92(B)(1). This point has been raised by several people; do you have any response?Now ask yourself. Without the neutral, is the metallic conduit path "Bonded"?
OK, good, your issue is the two paths. You obviously feel that the difference in requirements for the two ends of this service nipple presents a hazard. However, the NEC and the community does not see it that way. Do you have any evidence or examples of this hazard? Why is having a higher impedance fault path in parallel with a low impedance fault path a hazard? (1)
I think the discussion will be easier to follow if you adopt the common usage of "bonded" as refering to an object, not a path. I would suggest a different terminology for what you are advocating, like "I feel it is not enough for the nipple to be bonded, bonding should be required at both ends." (2)
As a definition of "bonded", this NEC definition leaves a lot to be desired. It is really only a definition of "bonding". The definition of "bonded" based on this is "having bonding to the common reference point", which would be the GEC or thereabouts. (3)
This doesn't really matter, because the grounded service conductor is explicitly allowed to be used for bonding in 250.92(B)(1). This point has been raised by several people; do you have any response? (4)
Cheers, Wayne