LarryFine
- Henrico County, VA
- Electrical Contractor
I agree.yeah....I'm confused..........Any thoughts?
Yes, mixing 14 with 12 with no tags = 'a bit squirrelly'.
see post #36
Here's the problem [you didn't think about] - as an inspector I don't know what your plans are;
in the many times I've seen 14 mixed with 12 for switch legs, the contractor had every intention of putting this on a 20A ckt;
If I did give this a 'pass' with no label in the panel, come final this work is closed up, I've been to 100's of other inspections since your rough, how am I supposed to remember that this one ckt needs special attention [15A breaker with 12 wire]... you would prob. forget as would I.
I know it is often impractical for you to sit around waiting for the inspector, but if you are going to do something a bit 'squirrelly', then you need to be on the job so we can agree on the work. In situations like this I just ask you to mark your NM [in the panel] "15A ckt only". But if you are not there to do this, we will prob. both forget about it come final.
I don't give my cell phone number to a lot of people. I don't want everyone calling me & asking "if this is ok, what should I do, etc". Nuisance calls.What an inspector should have done here is leave a note and cell number (yes it works both ways) and told him that your holding off on passing this job untill he calls you to exsplain what might become a violation.
Instead, I'll write on the permit card & enter into the computer....Such & such circuit is required to have a 15 amp breaker due to #14 wire in circuit.
While I agree, my phone has several ringtones. The most obnoxious one is for my boss:grin:. I HAVE to answer that one. That said, when I'm on a job, I do my very best to give the customer my undivided attention. The other calls go to voice mail & I retrieve them asap.I have noticed often while the inspector is visiting my job he gets calls. All part of wearing that hat.
Most of use just tell our wives not to call us at work. :grin:While I agree, my phone has several ringtones. The most obnoxious one is for my boss:grin:. I HAVE to answer that one.
Wont help him a bitI still would call his boss
You should set his ring to play the Pray for the Dead song.While I agree, my phone has several ringtones. The most obnoxious one is for my boss:grin:. I HAVE to answer that one.
He may have liked my splice-on-a-#14 idea after all.So he told me something I was going to do all along . . .
...What an inspector should have done here is leave a note and cell number (yes it works both ways) and told him that your holding off on passing this job untill he calls you to exsplain what might become a violation....
I disagree here. A good inspector would not say a thing, but make a notation on his paperwork. Then, on the final all he would need to do is check that circuit to ensure it had proper (15 A) overcurrent protection. If that was the case, then the final would not be affected, either.
Only if he found the improper protection (20 A) when performing the final should the issue even be mentioned.
For the project to move on, I changed out the #12 in the circuit to #14(so now entire ckt is #14)...Passed reinspection today.....Left note for inspector stating "For future reference, which NEC or local code was last week's rough-in failure in violation of?
He wrote on my note "Wire table 316 14 wire to be fused at 15amps."
WOW! So he told me something I was going to do all along and avoided telling me which code was violated by mixing #12 and #14 wire in a circuit. Also, is there even a table 316?